This document contains a question and answer log from a pre-solicitation conference for a small business set-aside contract to provide inspection, testing, and maintenance services for fire protection systems at Sierra Army Depot over a three year period. The services required include scheduled tasks for water-based fire suppression, dry chemical, wet chemical, and clean agent systems across sixty-one facilities. Questions and answers provide additional details on the types and quantities of specific systems such as five Pemall HFC-227 clean agent tanks and one Fire Trace HFC-227 tank, double check backflow preventers, and an Edwards Vigilant fire alarm system with AES monitoring. Annual inspections are due by March 31, 2022 for fire alarm and suppression systems, with five-year inspections due in 2023.
View the file
Other files
On GovTribe
Work with this file
- Download the original file
- Contacts named in this file
- Similar government files
- Ask GovTribe AI about this file
Text version
SIAD Fire Protection
W912GY-20-R-0013
Question & Answer Log
Document Document
Reference
Question/Comments Answer/Response Date Received Date Posted
Solicitation N/A Since the requirements for testing changes depending on the cycle of testing we would like to ask what years are the fire alarm and sprinklers on. Or in other words based on the table 2-2 and 2-3 what frequency of testing will have to be done in each year of the contract?
In table 2-2 and 2-3 there is a frequency (Annual is done yearly, Building inspection
Annually). Year one for the most part started in 2018, so in
2023 a 5-year will be required
(along with the pervious years options), unless it is a new system then the inspections tags will dictate it’s inspection year.
12 MAR 2021 16 MAR 2021
Solicitation N/A How many backflow are to be tested as part of this solicitation? How many
Reduced Pressure Backflow? How many
Double Check Backflows? When was the last 2yr and 5yr inspections performed on each backflow?
In Table 6.1 in the
W912GY20R0013 Solicitation all the backflow are indicated with “*”. There are several buildings that have two risers that are connected to one backflow device. All backflows are double check, we do not have any pressure reducing.
12 MAR 2021 17 MAR 2021
Solicitation N/A Do you have clean agent system reports that provide information on size of system and number of devices? Agent Type?
Agent Tank Size?
Clean agent systems are indicated on Table 6.1 in Part
VI. Each tank is equipped with
Pemall HFC-227(5 X Model
PCA 140-24) and Fire Trace
HFC-227 (1 X Model # FTF
000375).
12 MAR 2021 17 MAR 2021
Solicitation N/A How many tanks and links for the kitchen hood systems? Can these systems be tested during normal hours? If not which one will require after hours testing?
The amount of tanks and links differ for each kitchen hood system. Each kitchen has no less than 3 links and no more than 7 links. The Kitchen Suppression systems can be tested during normal hours or after business hours, when scheduled with the
COR.
12 MAR 2021 17 MAR 2021
Solicitation N/A Do you have a list of fire alarm devices to be tested such as horns, strobes, smoke detector, heat detectors, etc? When is the annual fire alarm inspections due?
Fire alarm panels have many different devices to be tested such as horns, strobes, smoke detector, heat detectors. There are 77 fire alarm systems on the depot, is there a specific building that they would like to know the amount of devices? It is a little excessive and manpower extensive to count all the device in every building.
Annual fire alarm inspections are done with the Fire
Suppression and that is due by
March 31, 2022.
Solicitation N/A When are the annual fire Wet/Dry sprinkler inspections due?
Annual fire alarm inspections are done with the Fire
Suppression and that is due by
March 31, 2022
12 MAR 2021 17 MAR 2021
Solicitation N/A Can you provide the sign in sheet for the site visit?
Sign in sheet was provided during the contractor visit.
12 MAR 2021 17 MAR 2021
Solicitation N/A What is the fire alarm reporting system that is used? AES, Monaco, Kingfisher?
The Fire Alarm system is a
Edwards Vigilant panel with an
AES transceiver and micro-key dispatch software.
Solicitation N/A When are the 5yr, 10yr, 20yr and 50yr sprinkler inspections due? When were they last completed?
5yr is due 2023 for most systems. A full inspection was performed in 2018 and that was the start of year one. However, there are systems that are newer and the inspection tags will provide you more data on the year the system maintenance is
on. Gauges and tanks shall be evaluated by the manufacture date.
12 MAR 2021 17 MAR 2021
Solicitation N/A When are the 5yr fire alarm inspections last performed?
5yr is due 2023 for most systems, however the inspection tags will provide you more data on the year the system maintenance is on.